Jimmy Backflow
Jimmy Backflow
  • Видео 18
  • Просмотров 620 174
Testing Backflow Preventers on Fire Systems Without Closing the Control Valves
Can you perform the protective aspects test on backflow perverters installed on fire systems without closing the upstream or downstream control valves? The answer is Yes, provided there is no downstream demand, and if testing a DCVA, there is no backpressure at test cock four. You may already be performing this test; it is nothing new; it is just using existing hydraulic principles.
Просмотров: 655

Видео

DCVA Analyzing Test Results - Assessing Backpressure
Просмотров 667Год назад
Assessing for backpressure before testing a DCVA. Part 1 Analyze the test results!
Pressure Vacuum Breaker - Testing Instructions
Просмотров 1 тыс.Год назад
How to test a pressure vacuum breaker using a three-valve test kit. This is a classroom instructional video.
Backflow Prevention Device Assemblies - Test Cock Flushing
Просмотров 1 тыс.Год назад
Should you flush the backflow prevention device assembly's test cocks before or after closing the downstream shut-off valve (number two shut-off valve).
RPZ - Analyzing Test Results - First Check Valve Test
Просмотров 7 тыс.2 года назад
This video analyzes the test results of the reduced pressure principle backflow prevention device assembly First Check Valve. It reviews the no-flow validations test and the backpressure assessment procedure.
RPZ - Testing Instructions
Просмотров 9 тыс.3 года назад
This is a video of an actual classroom training demonstrating how to test a Reduced Pressure Principle Backflow Prevention Device Assembly on a white board. In the video there is a discussion testing the second check valve differential.
RPZ - Why It Discharges
Просмотров 3,5 тыс.4 года назад
What causes the Reduced Pressure Principle Backflow Prevention Assemblies to discharge water?
DCVA & Backpressure
Просмотров 5294 года назад
This video demonstrates what happens when testing a double check valve assembly with backpressure present and the downstream was not closed or not drip tight.
Spill-Resistant Pressure Vacuum Breaker - How it works
Просмотров 11 тыс.4 года назад
This video demonstrates how a spill-resistant pressure vacuum breaker functions to protect the potable water system.
Pressure Vacuum Breaker - How it Works
Просмотров 63 тыс.4 года назад
This is an instructional video on how a pressure vacuum breaker works to protects the potable water system.
RPZ - How it works
Просмотров 75 тыс.5 лет назад
How a Reduced Pressure Principle (RPZ) Backflow Prevention Device Assembly Prevents Backflow
Spill-Resistant Pressure Vacuum Breaker - Field Test
Просмотров 9 тыс.6 лет назад
This video shows how to test a spill-resistant pressure vacuum breaker using a three valve differential test kit.
RPZ - Field Test
Просмотров 68 тыс.9 лет назад
Testing a Reduced Pressure Principle Backflow Prevention Device Assembly with a three valve test kit.
Pressure Vacuum Breaker - Field Test
Просмотров 42 тыс.9 лет назад
Testing a Pressure Vacuum Breaker - This video shows how to test a Pressure Vacuum Breaker using a three valve differential test kit.
Double Check Valve Assembly - How It Works
Просмотров 125 тыс.9 лет назад
This video illustrates how a Double Check Valve Backflow Prevention Assembly functions.
Double Check Valve Assembly - Field Test
Просмотров 136 тыс.10 лет назад
Double Check Valve Assembly - Field Test
Cross-Connection Control Training
Просмотров 2,2 тыс.10 лет назад
Cross-Connection Control Training
Testing a Backflow Prevention Device - RPZ
Просмотров 66 тыс.12 лет назад
Testing a Backflow Prevention Device - RPZ

Комментарии

  • @user-rq7ii6rv6o
    @user-rq7ii6rv6o Месяц назад

    If you watched this and didn’t understand, don’t panic it usually takes some time to do, I watched a while ago and I was So lost , then i bumped in to some issues and look for it again now with more experience , and I can tell you is a great source of knowledge !! Also I’m happy that i finally understood the whole thing 😂

    • @JimmyBackflow
      @JimmyBackflow Месяц назад

      Thanks for watching and pleased that you found it helpful.

  • @eng.mohamedsaalan8395
    @eng.mohamedsaalan8395 Месяц назад

    I am searching about double check valve we can use it with Sulphoric acid 98.5 conc.

    • @JimmyBackflow
      @JimmyBackflow Месяц назад

      You need to consult with a manufacturer. They do make plastic backflow preventers.

  • @danieldunn6329
    @danieldunn6329 4 месяца назад

    Thank you for providing and explaining this information. Clear, informative and helpful.

    • @JimmyBackflow
      @JimmyBackflow 4 месяца назад

      Thanks for viewing the video and you comment.

  • @asyrafjusoh9645
    @asyrafjusoh9645 4 месяца назад

    Hello. Which one is the supply pressure? I don't quite understand that part.

    • @JimmyBackflow
      @JimmyBackflow 4 месяца назад

      The supply pressure is where the water enters the backflow preventer. It is the inlet pressure or the pressure at TC#1. Supply pressure is typically higher than the outlet pressure. Backpressure is the exception.

  • @bigbreakssportscards8613
    @bigbreakssportscards8613 6 месяцев назад

    Richie introduced me to you Jimmy. Thank you for all you do.

    • @JimmyBackflow
      @JimmyBackflow 6 месяцев назад

      Thanks for the comment and viewing the videos. I hope they were helpful.

  • @rickallen4138
    @rickallen4138 7 месяцев назад

    Had to go music distraction 😮

    • @JimmyBackflow
      @JimmyBackflow 7 месяцев назад

      The purpose of the video is to educate, entertain, and engage. Distractions are everywhere, so put them aside and concentrate on what is essential. You could turn off the sound.

  • @MB-dx9ku
    @MB-dx9ku 8 месяцев назад

    Great video and visual Thanks

    • @JimmyBackflow
      @JimmyBackflow 7 месяцев назад

      Thanks for viewing the video and your comment. Hope it was helpful.

  • @xKCphillipsx
    @xKCphillipsx 9 месяцев назад

    do the check valves close with the supply open and #2 shut off closed? I have one spring with 1lb force--> I have 10 psi coming in--> 1 pound lost while overcoming the spring ---> I now have 9 lbs on the downstream side of the check. At what point do I get higher on the down stream side to over come the supply and close?

    • @JimmyBackflow
      @JimmyBackflow 9 месяцев назад

      When the backflow preventer is in a static state no downstream demand the check valves are closed. When in a static state the pressure loss across the check valves is generated by the check valve springs. Typically, a minimum of one pound loss on each check valve. The check valves open when there is a flow through the device and a downstream demand. If there is a backpressure issue (higher pressure on the outlet side of the device) the second check valve should close drip tight if operating properly. I hope this answers your question and thanks for viewing the video. If you have any further questions, let me know.

  • @nef7939
    @nef7939 9 месяцев назад

    My favorite part is robot voice. I guess the test cocks are for show? You didn’t point out a single thing in this video

  • @tapalmer99
    @tapalmer99 10 месяцев назад

    Thanks so much for your video You've got great instructions without rushing through it I was going to build my own rig out of the differential gauge hoses and Associated fittings Can you recommend a website or video for doing that? Thanks again

    • @JimmyBackflow
      @JimmyBackflow 10 месяцев назад

      Thanks for the comment. I have not encountered a video for making a backflow test kit, but I have tried unsuccessfully. The differential gauge is available, but purchasing a test kit in the long run was more economical. Also, the test kit would have to be calibrated. Getting used test kits and parts is an option that I have used.

  • @gaigehamilton6257
    @gaigehamilton6257 11 месяцев назад

    Not related to any video in particular, as I’ve watched most by this point, but I wanted to say thank you. I’ve just completed testing for NEWWA and you have helped tremendously. Nolan speaks very highly of you, and I too would recommend your videos.

  • @biker55555
    @biker55555 Год назад

    Hi, when testing for a no-flow condition prior to testing the checks, does the no-flow test depend on the checks working? Thanks.

    • @JimmyBackflow
      @JimmyBackflow Год назад

      The video that you are referring to assesses backpressure. In this procedure, the check valves do not have to be drip tight. If they are not drip-tight the pressure at test cock four would be the same as test cock one. If backpressure is present. the downstream shut-off valve is not closed drip-tight and the pressure reading at test cock four is greater than the pressure at test cock one. Thanks for watching the video and I hope this answers your question.

    • @JimmyBackflow
      @JimmyBackflow Год назад

      When conducting the "no-flow validation test,' the differential pressure gauge must record a positive reading. Therefore, the check valve must be working to perform the test. However, the video that you watch is assessing backpressure. In this procedure, the assessment can be performed with non-working check valves.

  • @thesportsjerseyenthusiast7953

    Absolutely love the music can’t say it enough. Makes me want too test a backflow with class and style

  • @akmchefskingdom6607
    @akmchefskingdom6607 Год назад

    Gotdam your music is great.

  • @toxicwar
    @toxicwar Год назад

    Out of all the videos i've searched for to explain what the heck is a backflow safety valve. this one is the ONLY one that nails it with it's instructions and how it works. ThaNk you so much for satafying my 1am curiosity.

    • @JimmyBackflow
      @JimmyBackflow Год назад

      Thanks for the comment, and if you need any further information let me know.

  • @poundersforpresident604
    @poundersforpresident604 Год назад

    Very informative but please make one without the music. 😢

    • @JimmyBackflow
      @JimmyBackflow Год назад

      There is a video without music for testing the RP. Sorry, you did not like the music; I may remake the videos without music when I have time. I am presently working on other videos without music. Nonetheless, I hope you found the videos useful. Thanks for the comment.

  • @AndrewHarmless-wv5or
    @AndrewHarmless-wv5or Год назад

    I think its interesting how different states/cities require different ways of testing. I have watched several different videos of testing RPZ, DC and PVB and it seems no two are the same. I can test RP's and DC's with my eyes closed the way it is required in my state. PVBs are only allowed for Isolation here they cannot be containment or irrigation. In the past 5 years I have tested two. Getting re-certified again next week so trying to remind myself how to properly test them. We only use one hose to test where I am and we do the air inlet before the check valve. Appreciate the video anyways it is always intriguing to see other ways people test these assemblies and what is allowed. One thing I have noticed is no video ever marks recording the line pressure. I cant imagine my state is the only one that requires recording that but between the 3 assemblies I have never seen a video where someone mentions it. I beleive on the PVB test line pressure is recorded during the test for the check, not the air inlet. If you know the answer to this can you confirm? Thanks again video was fun to watch.

    • @JimmyBackflow
      @JimmyBackflow Год назад

      Andrew, thanks for the comment and watching the videos. There should not be a required test procedure because they are all identical. The test form does not indicate what procedure is used, it only asks for the differential pressure and does it meet the standard. All tests are the same; the only difference is the testing sequence. Every “procedure” measures the differential pressure to determine if the check valves are drip tight and if the assembly provides protection; they can be assessed in many ways, but again, the test should demonstrate the protective aspects of the backflow preventer. It is very unusual for a state to require a specific way of testing. I would question that requirement. Most states require the individual to be certified to perform the test. Regarding the line pressure - if you notice, the inlet pressure is noted when backpressure is assessed before testing the DCVA and RPZ. Just a note knowing the line pressure is not necessary when testing backflow preventers since it is a relative test-however, some forms require the recording of line pressure. Your correct line pressure can be recorded when conducting the PSID of the PVB check valve if there is a pressure gauge on the high-pressure hose. If not, use a standard pressure gauge like the one in the videos to measure line pressure.

    • @AndrewHarmless-wv5or
      @AndrewHarmless-wv5or Год назад

      @@JimmyBackflow I agree a testing procedure is a procedure. I have just out of curiosity tested assemblies in some of the other ways I've seen online and have gotten the exact same numbers as the ways my state teaches us to test. When initially getting certified 5 years ago before our practical test witnessed by proctor. I had been watching a lot of videos of testing so I would be fully prepared. I noticed it then the different ways tests would be done. I asked my proctor about it and he informed me "yes there are some 2 hose tests for this and single hose tests for that but only the way you are taught to test here is approved here." I am certified for my entire state, through training and municipal orientations. In the field if a meter is locked the municipality will send out someone from the cross connection department to unlock the meter and they have to witness you testing. They will quickly inform you if you miss a step or are about to. I have asked them as well have they ever seen the other ways assemblies are tested and they've all said yes however it is "not as accurate or approved here". Like I said though I have played around and done the different ways myself with the exact same numbers as our "approved" way. I will ask again this week when I get my re-certification and see what answer I get this time. I will let you know. Thank you for the reply you are very clearly well versed and knowledgeable, the name "Jimmy Backflow" would explain that haha.

  • @ridgerunner4420
    @ridgerunner4420 Год назад

    This was an excellent presentation on how these devices operate and what happens when they are compromised. Thank you for putting this together!

    • @JimmyBackflow
      @JimmyBackflow Год назад

      Thanks for viewing and for the comment!

  • @billhelmken5483
    @billhelmken5483 Год назад

    Great video. This is much easier to follow and understand when compared to the recertification courses. Thank you.

    • @JimmyBackflow
      @JimmyBackflow Год назад

      Thanks for the comment. Hope it helped with your recertification process.

  • @josemanuelguzmanconcepcion5793

    Hi, We have to perform 5 year internal inspection on Backflow ?

    • @JimmyBackflow
      @JimmyBackflow Год назад

      It is state dependent. What state are you working in. Some states require internal inspections but only on testable devices installed for service protection. New Jersey regulations require a Physical Connection Permit be obtained by the owner of a facility where the physical connection installation is to be made with a community water supply (Physical Connection Permits are not required for private residences). Physical Connection Permit has to be renewed annually and requires each backflow prevention device covered by the permit to be tested quarterly and internally inspected annually.

  • @robf4605
    @robf4605 Год назад

    This is why ABPA is the best. These testing methods are garbage.

    • @JimmyBackflow
      @JimmyBackflow Год назад

      Rob F. Please provide a more detailed statement regarding your comments. What are your qualifications for making such a statement? All test procedures measure the pressure loss across the check valve. The only difference is the sequence by which the tests are conducted. In the video, the first check valve differential is measured, the second check valve is back pressured, a validation test is preformed, and the relief valve is opened by introducing pressure into the zone. Also, which is not conducted by ABPA is the differential test of the second check valve. ABPA does the same but in a different order. I suggest you read up on how backflow prevention device assemblies are tested to confirm reliability. Let me know if you would like further training!.

    • @robf4605
      @robf4605 Год назад

      @JimmyBackflow guess you're not familiar with abpa. Nor with the terminology. Been a tester in the city of sioux falls for over a decade along with asse, Iowa and Nebraska specific. Also having no problem reading USC cross connections 9th or 10th edition. You should try multiple classes from multiple providers. Quit being so close minded. I watched your video and just felt a little sorry for you. Have a good one.

    • @JimmyBackflow
      @JimmyBackflow Год назад

      @@robf4605

    • @JimmyBackflow
      @JimmyBackflow Год назад

      @@robf4605 Rob, not sure where you are going with this, but you need to be more specific as to comments. Pay more attention to the testing aspects and less time criticizing what you do not know. Stop guessing! Read page 255 FFCCCHR 10th addition. The difference is the sequence of the tests. I am very familiar with all certification programs and provide instructions in all aspects of the testing methos taught by APBA instructors. I am very familiar with the methods stated in the USC Manual of Cross-connection Control. I provide instructions on all test methods in my training. I am not sure what you mean by being close minded because I am not sure what your problem is with the video. Please in the future provide constructive criticism --- I am not interested in your nonconstructive opinions. As you suggested, --- I have attended training from other certification programs and held certifications from several states and certification organizations. (Been around for a long time) The method in the video is taught by trainers throughout the New England states, NY, PA, and NJ. This method is listed in the AWWA M14 Manual and follows ASSE 5000. Why are you feeling sorry for me? (Strange statement!)

    • @robf4605
      @robf4605 Год назад

      @JimmyBackflow lol, it's testing backflows. Possibly the easiest thing I've ever come across that you can get paid for. I'm just giving you shit. Just keep doing what you're doing bud.

  • @JohnBaker3000
    @JohnBaker3000 Год назад

    Perfect explanation. Thank-you!

  • @samiamcrow9454
    @samiamcrow9454 Год назад

    Actually if back pressure is a possibility, the device should be replaced with an RPZ.

    • @JimmyBackflow
      @JimmyBackflow Год назад

      The DCVA is approved for backpressure situations. I refer you to ASSE, USCFCCCAHR and AWWA. What are the bases for your statement?

  • @Al-po2oh
    @Al-po2oh Год назад

    What is the purpose of the distracting music?

    • @JimmyBackflow
      @JimmyBackflow Год назад

      For your entertainment and to keep you interested. In addition, it keeps other trainers from steeling my work. I like music. Nonetheless, I hope you learned the art of testing a PVB. Thanks for viewing the video and commenting.

  • @roberte.6892
    @roberte.6892 Год назад

    This video is another great example of how to instantly ruin all your hard work with an annoying, loud, distracting song. Bleh ...

    • @JimmyBackflow
      @JimmyBackflow Год назад

      Robert by your comment I take it that you are not a music lover but thanks for the comment. I enjoy all types of music and like to incorporate music into my training to make the videos more interesting. Nonetheless, I hope you gained some knowledge by watching the video and I hope you continue to watch other videos. If you do turn down the sound. As the song goes "you can't please everyone, so you got to please yourself."

  • @Drak7282
    @Drak7282 Год назад

    Excellent video, needs better background music. 12 minutes of that is enough to make you want to jump off a building lmao

  • @KaneBannanas
    @KaneBannanas Год назад

    Ingenious design

  • @ford23f150
    @ford23f150 Год назад

    Great video. Just took the backflow prevention device tester training course at nwwa with as the teacher. Did a awesome job teaching the material would recommend taking the course if you want to become a backflow tester.

  • @MarcHess
    @MarcHess Год назад

    Excellent detailed analysis!

  • @adamanderson7761
    @adamanderson7761 Год назад

    Thanks, that was interesting.

  • @wyleaziz5050
    @wyleaziz5050 Год назад

    Nice and easy demonstration!

  • @chrisperkins3774
    @chrisperkins3774 2 года назад

    Asking to understand, not to criticize. If the water pressure is reduced as it goes through the check valves, why isn’t the non- potable pressure reduced in a back pressure, backflow condition?

    • @JimmyBackflow
      @JimmyBackflow 2 года назад

      Backpressure is greater than the inlet pressure and is prevented from flowing into the potable water system by a closed second check valve. If the second and first check valves are not drip tight, the backpressure non-potable water will lose pressure due to friction factors as it flows in the unwanted direction. When water flows through the backflow prevention device assembly, the pressure loss is due to the spring-loaded check valves. If both check valves are not holding drip tight against backpressure, the check valves are open, and the check valve springs are not creating the pressure loss with the water flowing in the unwanted direction. With backpressure, some pressure loss may be present in the body of the assembly but insignificant.

    • @chrisperkins3774
      @chrisperkins3774 2 года назад

      @@JimmyBackflow I got ya. Love the content of your videos and appreciate you making them. Thank you for taking the time to reply my question.

  • @winstonsaxonsdad
    @winstonsaxonsdad 2 года назад

    I have an older irrigation system installed at my home. I have access to the outgoing pipe to the sprinkler in the basement. From there, it goes to a free-standing verticle PVC pipe with a sill cock on it, and on top of that is a schrader valve, that the irrigation companies uses to blow out the water before winter. There is no backflow preventer installed. My question is this. Since it appears to install a backflow preventer, I need access to the outgoing water line. I do have that access inside the basement but on the outside, if I were to install the backflow preventer there, I believe I would have to dig down to get access to the pipe after it leaves the sillcock and heads to the valve box. Is that correct? I don't believe I can install it on the vertical free-standing PVC pipe since not only does water come out there, but also the air pressure is attached there to clean out the irrigation lines. I have seen screw in backflow preventers but not sure that would work. Any suggestions would be appreciated. Thanks

    • @JimmyBackflow
      @JimmyBackflow 2 года назад

      You can install a pressure vacuum breaker on the PVC vertical line that leads to the sprinkler system, providing that the pressure vacuum breaker is 12 inches above the highest sprinkler head. Without seeing a diagram, I can't say for sure what is the best solution.

  • @JonnnyStorm
    @JonnnyStorm 2 года назад

    5:22 , does this mean the water can flow from low psi to high psi from the direction of left to right?

    • @JimmyBackflow
      @JimmyBackflow 2 года назад

      Jonnny, no water flows from high to low pressure --- from left to right in this diagram. If backpressure is present downstream on the right side of the slide, this is now the high-pressure side. In this case, if operating correctly, the second check valve prevents the high pressure from flowing back into the inlet pressure. If a backshphonage situation is occurring in the inlet system, the pressure is subatmospheric and the pressure downstream of the backflow device assembly is atmospheric. The first check valve prevents non-potable from entering the system is operating correctly. The flow is from high to low.

  • @MrRickyt88
    @MrRickyt88 2 года назад

    Thanks for the video. The fix where test cock #4 has higher pressure on the first test would be just to replace the shutoff valve right? I guess we could try opening and closing a few times also to see if it releases something that might’ve been lodged.

    • @JimmyBackflow
      @JimmyBackflow 2 года назад

      Yes. Rick, if backpressure is present at test cock number four, the downstream shut-off valve is not drip tight. Try reclosing. If the backpressure does not diminish, replace, or repair the downstream shut-off valve. Test the assembly if you can eliminate the backpressure.

  • @connpiper
    @connpiper 2 года назад

    Hey Jimmy, new to testing. Bought a couple bfps to practice on. Working on rpz, 3/4. Long story short, cleaned seals and seats on check#1 and relief. No drips when shut off downstream valve. When testing differential on check 1, relief opens when bleeding high side. Any help greatly appreciated.

    • @JimmyBackflow
      @JimmyBackflow 2 года назад

      Not to worry. What is happening is you are diverting high-pressure water away from the sensing line which is keeping the relief valve closed when you open the high control valve on the test kit. Test cock number two is close to the sensing line. Close the high control valve and continue with the test.

    • @connpiper
      @connpiper 2 года назад

      @@JimmyBackflow should have stated, relief opens after shutting high side after bleeding air. So test would still be valid then? Thanks for your time,help,response.

    • @JimmyBackflow
      @JimmyBackflow 2 года назад

      @@connpiper If water did not discharge from the relief valve after closing the downstream shut-off valve, the first check is holding drip tight provided that the RP was in a static state. If after bleeding the air out the high side of the test kit and the relief valve discharged and stopped, fluctuating inlet pressure was the cause. Continue with the test.

    • @connpiper
      @connpiper 2 года назад

      Thank you Jimmy.

  • @jeonghwanbae2111
    @jeonghwanbae2111 2 года назад

    Thank you for a detail explanation of a backflow testing. Is it possible to make a simple testing tool for DIY purpose of check valve # 1 and #2 testing like using a evaluate for backpressure as you made ? I barely passed check valve #1 testing in last year and i failed check valve #2 with leaking. I think it was from o-ring on seat kit and I replaced it. I am sure it is ok now. But I don't know 100% if it is ok. Pluming company charge $150 for just testing. Would you please help me out to save the testing cost. Thanks

    • @JimmyBackflow
      @JimmyBackflow 2 года назад

      Thanks for watching the video. Simple test. To measure the differential pressure across the DCVA, check valves, close the downstream shut-off valve, and connect a standard pressure gauge (200 psi) to test cock #2. Open the test cock and record the pressure reading. Close test cock #2, remove the gauge, and connect it to test cock #3. Open test cock #3 and record the reading on the gauge. Subtract test cock #3 reading from test cock #2 reading. The pressure loss across the first check valve must be one psi or greater. For the second check valve differential, conduct the same steps using test cock #3 and #4. The pressure loss across the second check valve must also be one psi or greater. This procedure works, providing there is no downstream demand.

    • @jeonghwanbae2111
      @jeonghwanbae2111 2 года назад

      @@JimmyBackflow Thank you for your answer. Actually I have watts LF909 and i know the Backflow is tested on RPZ. Is it same way to test #1&2 check valve for RPZ ? I am not sure if you receive my email. Please see it and kindly reply when you are free. Thank you again.

    • @JimmyBackflow
      @JimmyBackflow 2 года назад

      @@jeonghwanbae2111 A simple test for the RPZ would be to follow the procedure previously stated to confirm the DCVA check valves. To test the opening point of the RPZ, connect a pressure gauge with a bleed attachment as seen in the DCVA video (best to use 0 to 100 Psi or less) to test cock #2. Open test cock #2. With the gauge reading pressure, close the upstream and downstream shut-off valves. Next, open test cock #3. When the water stops flowing out of the test cock, the gauge reads the static pressure upstream of the first check valve. Next, open the bleed valve on the pressure gauge. Water discharges out of the relief valve, and the gauge reads the opening point of the relief valve.

    • @jeonghwanbae2111
      @jeonghwanbae2111 2 года назад

      @@JimmyBackflow Thank you so much. I measured the pressures for each cock #2&3&4 and found the differences between them. I tried to measure 2&3 in one time per your class but I am in difficulty to find correct gauge with my tool. I am going to send 4 pictures showing the pressure of each cock for your advice, if you don’t mind. Thanks

  • @JorgeRuiz-jk5vn
    @JorgeRuiz-jk5vn 2 года назад

    I can't think clearly with the dum backround music. I can't listen to your instructions clearly. Wby is there music.

    • @JimmyBackflow
      @JimmyBackflow 2 года назад

      I can see clearly now, the rain is gone I can see all obstacles in my way Gone are the dark clouds that had me blind It's gonna be a bright (bright), bright (bright) Sun-shiny day. (Johnny Nash) I like music and my purpose is to educate, entertain and engage. if you watched the complete video, you would have noticed that at the time of the test, the music was muted. it is possible to learn how to test a backflow preventer by just watching without the sound. Just pay attention to what is being done. I will provide you a copy of the written instructions if you provide me with your email address. Jorge, sorry you did not like the music.

    • @JamesBond-kb1wl
      @JamesBond-kb1wl 3 месяца назад

      I was just about to leave the same comment. Ruthless music at that. Makes me suicidal

  • @JesusCow
    @JesusCow 2 года назад

    nice

  • @jeffwrinkle575
    @jeffwrinkle575 2 года назад

    What is the purpose of the TC#1, TC#2, TC#3 and TC#4?

    • @JimmyBackflow
      @JimmyBackflow 2 года назад

      TC#1 is typically used for maintenance purposes and can be used to create a static state when the downstream shut-off valve is not drip tight. The purpose of TC#2 is to measure the pressure upstream of the first check valve. The purpose of TC#3 is to measure the pressure downstream of the first check valve and upstream of the second check valve. The purpose of TC#4 is to measure the pressure downstream of the second check valve. By knowing the pressure upstream and downstream of the check valve one can determine the pressure loss across the check valves. The differential pressure across the check valves of a DCVA shall be 1PSID or greater to comply with the industry standards. I suggest you view the testing videos for further information on testing.

  • @lisafamiglietti4050
    @lisafamiglietti4050 2 года назад

    Hi Jimmy, I represent a company call Safe T Cover and we would like to use this video in an upcoming blog we have scheduled. Please let me know if have permission to link to your video. Thank you.

    • @JimmyBackflow
      @JimmyBackflow 2 года назад

      Yes, sure ---- Use any of the videos. I use these videos to promote my online cross-connection control and backflow tester training offered at www.ceuplan.com.

  • @fraza7977
    @fraza7977 2 года назад

    Thanks for the video, will you be doing a part 2 for the second check valve?

    • @JimmyBackflow
      @JimmyBackflow 2 года назад

      Yes, and the third part will be the relief valve.

  • @conqwiztadore2213
    @conqwiztadore2213 2 года назад

    Where does the Z come from lol. Video isn't bad. Thank you

    • @JimmyBackflow
      @JimmyBackflow 2 года назад

      The "Z" stands for the area between the first and second check valve "the Zone" - Some manufacturers refer to this type of backflow preventer as a "Reduced Pressure Zone Assembly" while other manufacturers refer to them as a "Reduced Pressure Principle Assembly"

    • @humblethinker8493
      @humblethinker8493 Год назад

      @@JimmyBackflow oh wow, this comment was really helpful! Thanks!

  • @peralta9567
    @peralta9567 3 года назад

    Can you have check valves down stream of the pressure vacuum breaker to prevent back pressure from a irrigation drip line up about 30 feet?

    • @JimmyBackflow
      @JimmyBackflow 3 года назад

      Very interesting question! Not sure that a drip line will create backpressure since the drip line will be subjected to the atmosphere pressure. Therefore no need for a check valve to prevent backpressure. However the installation of the check valve will not impact the operation of the pressure vacuum breaker. The pressure vacuum breaker can be subjected to pressure downstream that is less than the inlet pressure. So as long as the pressure downstream of the pressure vacuum breaker is less than the inlet pressure it will work just fine with regular maintenance and testing.

  • @Kevin-Schmevin
    @Kevin-Schmevin 3 года назад

    This shit is terrible

    • @JimmyBackflow
      @JimmyBackflow 3 года назад

      Thanks for viewing the video, and you insightful comment -- I hope you learned something.

  • @H2OMANLV
    @H2OMANLV 3 года назад

    Dude, you need to go back and re-read the USC 10th edition .much incorrect info.

    • @JimmyBackflow
      @JimmyBackflow 3 года назад

      Dude you fail to understand how pressure vacuum breaker works --- just because the steps are not the same it does not mean that the test of the pressure vacuum breaker was not conducted correctly. This is not the USC 10th edition video on how to test a pressure vacuum breaker but it is a video that effectively demonstrates the operational condition of a pressure vacuum breaker. As a tester you should understand how a pressure vacuum breaker functions and what is required to perform test to determine that the pressure vacuum breaker is providing protection. The test of the check valve and air inlet valve are performed the same way as the USC 10th edition but conducted in a different sequence. A well trained tester should be able to see that the process of testing is the same. Test the check valve to determine that is closes drip tight and test the air inlet valve to determine that is opens. The test is conducted during a static state. Understanding how a backflow prevention device functions is critical in the understand of how and why the test are performed. Keep reading to understand what you are required to do to perform the test. Just reading the instruction without understand what is being done does not make for a good tester. Thanks for viewing the videos and you comments. I hope viewing the video caused you to think about what you are actually doing when conducting the tests.

    • @JimmyBackflow
      @JimmyBackflow 3 года назад

      This video shows how to measure the differential pressure across the check valve by my measuring the pressure at test cock number one and test cock number two. The test kit calculates the difference. This procedure is conducted as the PVB is in a pressurized state. Note that the upstream shut-off valve is in an open position. The procedure that you are referring to and most likely taught, measures the pressure at test cock number one while removing the pressure downstream of the check valve. The test kit does not calculate the difference in pressure but measures the pressure at test cock number one. I both cases the pressure reading shall be 1 PSID or greater. Both way are industry acceptable. In both test procedures the air inlet valve opening point is measured by removing the pressure upstream of the air inlet valve and downstream of the check valve, simulating a backsiphonage situation. Hope this helps you better understand the process of conducting the test of a pressure vacuum breaker.

  • @LorenzKamo
    @LorenzKamo 3 года назад

    A+

  • @TheGardista
    @TheGardista 3 года назад

    Good job 👍

  • @twtw2247
    @twtw2247 3 года назад

    Very good video shoes how the rp works and how to test properly and why thumbs ☝

  • @misterphoenix3684
    @misterphoenix3684 3 года назад

    thank you!